Question: Consider an enclosed swimming pool. The pool area has a sensible heat loss of 4 2 4 , 0 0 0 B t u h

Consider an enclosed swimming pool. The pool area has a sensible heat loss of
424,000Btuh and a latent heat gain of 530,000Btuh on a design day when the outdoor
air is at 35 F and 20%RH. The space is to be maintained at 75 F and 50%RH. Outdoor
air is heated to 60F, mixed with recirculated air from the conditioned space and the
mixed air heated to supply conditions. Draw the diagram of the HVAC system
Questions -
(a) At what rate in cfm, is the air supplied to the space if the supply air temperature is
95 F?-(ANSW -20,714 cfm)
(b) At what rate, in cfm, is outdoor air flowing if recirculated air is 6,646 cfm?-
(ANSW -12,922 cfm)
(c) What is the heat transfer rate for the preheat process? -(ANSW -355,098 Btu/h)
(d) What is the heat transfer for the mixed air heating process? -(ANSW -635,998
Btu/h)