Question: General lighting and receptacle load = 3 8 0 0 * 3 = 1 1 4 0 0 VA Small appliance branch circuit load =

General lighting and receptacle load =3800*3=11400 VA
Small appliance branch circuit load =1500*3=4500 VA
Laundry =1500*1=1500 VA
Total General Lighting Load =11400+4500+1500=17500 VA
Receptacle load =175003000=14500 VA *0.35 demand factor =5075 VA where 3000 VA is first VA @100%
Total Demand Load =5075+3000=8075 VA.
2.
Water Heater: 28,000 VA, Dishwasher: 1,200VA, Food Disposal: 1,200 VA, and Attic Fan: 1,500 VA.
Total Appliance Load: 28,000+1,200+1,200+1,500=31,900 VA
Fixed in Place Appliance Load: 31,900 VA *0.75=23,925 VA.
3.
Dryer Demand Load line =5000 W (VA)*100% VA =5000 VA
Neutral =200 A
4.
Cooking equipment demand load =2(3kW) and 6kW cooktop
Total demand load (3kW *2units *0.75)+(6kW *0.8)=9300 watts
Neutral =400A
5.
HVAC Demand load =(240V *17.9A)+(240V *3.3A)=5800 VA
6.
Large Motor demand load =.25*1600VA =400 VA