Question: How to solve using calcuator. Please write the equation. Two mutually exclusive alternatives for office building refrigeration and air conditioning are being investigated. Their relevant

How to solve using calcuator. Please write the equation.
Two mutually exclusive alternatives for office building refrigeration and air conditioning are being investigated. Their relevant costs and lives are summarized as follows: If the hurdle rate (MARR) is 15% per year and the study period is 18 years, which chilling system should be recommended?
\table[[,\table[[Absorption],[Chilling (AC)]],\table[[Compression],[Chilling (CC)]]],[Capital Investment,$60,000,$80,000],[\table[[Annual Operating],[Expenses]],40,000,32,000],[\table[[Salvage (market)],[value]],10,000,0],[Useful Life,6 years,9 years]]
Step 4
Compute of EUAC for both types of compression (Absorption Chilling (AC Compression Chilling (CC)) is calculated below:
EUACAC=-$40,000-$60,000(AP,15%,6)+$10,000(AF,15%,6)
=-$40,000-$60,000(0.2642)+$10,000(0.1142)
=-$54,710
EUACCC=-$32,000-$80,000(AP,15%,9)+0
=-$32,000-$80,000(0.2096)
=-$48,768
Thus, the EUAC for AC and CC is $54,710 and -$48,768 respectively.
On the basis of EUAC, Chilling Compression should be recommended.