Question: Part # 4 Final Power Factor Correction Determine the amount of apparent power that would produce the desired power factor to correct this new value

Part #4 Final Power Factor Correction
Determine the amount of apparent power that would produce the desired power factor to correct this new value to 0.95. A WYE connected capacitor bank will be installed.
VAdesired=PpresentPFdesired
Determine the amount of reactive power that would produce the desired amount of apparent power.
VARsdesired=((VAdesired)2-(Ppresent)2)2
Determine the capacitive VARs necessary to produce the desired reactive power. VARsCneeded=VARspresent-VARsdesired
Determine the amount of capacitive current necessary to produce the capacitive VARs needed.
IC=VARsCneededEL32
Part # 4 Final Power Factor Correction Determine