Question: Problem: Eccentrically Loaded Spread Footing A 1 4 - ft 1 1 - f t 3 6 thick footing supports a 2 4

Problem: Eccentrically Loaded Spread Footing
A 14-ft 11-ft36" thick footing supports a 24"16" column and is subjected to the following service loads and moments: D=350kip,L=250kip,MD=80k-ft,ML=100k-ft If the footing is reinforced with 15#7 bars bottom in the long direction, check the adequacy of the footing under the eccentric loading in the long direction. The Geotechnical report specifies a net allowable soil pressure of 4700 psf. Assume
f'c of 3500 psi and fy of 60,000 psi. Neglect the weight of the footing. Assume adequate development length and the equation governing for 2-way shear is the same as in Example 10-5.