5 pts
We have a 21 relay installed in substation a looking over Line A-B, as well as Line B-C and Line C-D as backup protection.
Line A-B length is 44 km .
Line B-C length is 107 km .
Line C-D length is 56 km .
ZLine =0.033 per km.
In the 21 relay we need to program the impedance for the Zone 3 reach. From the given information above, calculate the primary impedance that the Zone 3 will reach to.
Hint: Primary impedance is the actual impedance of the line, so you do not have to take into account the CT and VT at this point.