Question: Required information The resistance values in the given table are calibrated for operation at 20C. They may be corrected for operation at other temperatures
Required information The resistance values in the given table are calibrated for operation at 20C. They may be corrected for operation at other temperatures using the relationship R 234.5+T R 234.5+T where T1= reference temperature (20C in the present case) T2 desired operating temperature R1= resistance at T1 R2= resistance at T2 A piece of equipment relies on an external wire made of 28 AWG soft copper, which has a resistance of 58.0 Q at 20C. Unfortunately, the operating environment has changed, and it is now 108.5 F. Cross-Sectional Area Conductor Size (AWG) (mm2) Ohm's per 1000 ft at 20C 28 0.0804 65.3 24 0.205 25.7 22 0.324 16.2 18 0.823 6.39 14 2.08 2.52 12 3.31 1.59 6 13.3 0.3952 4 21.1 0.2485 2 33.6 0.1563 alculate the length of the original wire. (Round the final answer to three decimal places.) he length of the original wire is 888208 ft.
Step by Step Solution
There are 3 Steps involved in it
Get step-by-step solutions from verified subject matter experts