Question: The temperature is measured using a sensor and a transmitter, TT 2 2 , that sends the measurement to a corresponding controller, TC 2 2

The temperature is measured using a sensor and a transmitter, TT 22, that sends the
measurement to a corresponding controller, TC 22, that compares the actual temperature
with a desired temperature set point, SP. The controller automatically opens or closes a
valve to allow or prevent the flow of steam to change the temperature in the tank. The
corresponding block diagram for this system is shown in the figure part (b).
Assume the following transfer functions:
G_(v)(s)=(0.02)/(4s+1)
G_(p)(s)=(70)/(50s+1)
H(s)=(1)/(12s+1)
(a) Assuming Gc_(c)(s)=K, find the value of K that will result in a dominant pole with \zeta =0.7.
Obtain the corresponding T_(s).
(b) Design a lead compensator to obtain the same damping factor as Part (a) but with a
settling time 20% smaller.
(c) Verify your results with MATLAB simulation.
Hint: the value of GH(s) to use in the rlocus command is:
GH(s)=(1.4)/(2400s^(3)+848s^(2)+66s+1)
Provide the derivation to obtain the GH(s) shown in this Hint. Problem 3(Chapter 9):
Lead controller:
The figure part (a) shows a heat-exchanger process whose purpose is to maintain the temperature of a liquid at a prescribed temperature.
(a)
The temperature is measured using a sensor and a