Question: Three physically identical synchronous generators are operating in parallel. They are all rated for a full load of 3 MW at 0 . 8 PF

Three physically identical synchronous generators are operating in parallel. They are all rated
for a full load of 3 MW at 0.8 PF lagging. The no-load frequency of generator A is 61 Hz, and
its speed droop is 3.4 percent. The no-load frequency of generator B is 61.5 Hz, and its speed
droop is 3 percent. The no-load frequency of generator C is 60.5 Hz, and its speed droop is
2.6 percent.
(a) If a total load consisting of 7 MW is being supplied by this power system, what will the
system frequency be and how will the power be shared among the three generators?
(b) At what load does one of the generators reach to no-load condition? Which generator
reaches to no-load condition first?
(c) At what load does one of the generators exceed its ratings? Which generator exceeds its
ratings first?