Question: Use a dead load factor of 1 . 2 5 and live load factor of 1 . 5 . Use the Canadian Metric rebar sizes

Use a dead load factor of 1.25 and live load factor of 1.5. Use the Canadian Metric rebar sizes Design a square tied column 5.5m tall with loads LL=1,881kN and DL=3,678kN using Fy=
414MPa steel and fc'=35MPa concrete. We will assume that the column has no intermediate
bracing and has an effective length factor K=1.0.
Design load:
1.6(1,881kN)+1.2(3,678kN)=7,423.2kN
Tied column design formula:
Pmax=R(0.65)(0.8)Ag[0.85fc'(1-pg)+Fypg]
Assume that R=1,pg=0.03.
7,423,200N=1.0(0.65)(0.8)Ag[0.85(35MPa)(1-0.03)+4,141MPa(0.03)]
Ag=7,423,200(N)1.0(0.65)(0.8)[0.85(35MPa)(1-0.03)+414MPa(0.03)]
=7,423,200(N)0.52[29.75-0.892+12.42MPa]=345,839mm2
We have specified a square column; therefore:
d=345,839mm22=588mm=600mm
Ag=360,000mm2
Radius of gyration r=0.3(600mm)=180mm.
Slenderness ratio KLr=(1.0)5,500(mm)180(mm)=30.528
R must be calculated.
R=1.07-0.008Lr=1.07-0.0085,500(mm)180(mm)=0.83
Since R is not as assumed in step 1, the actual required pg must be found by solving the col-
umn equation.
Pmax=R(0.65)(0.8)Ag(0.85fc'(1-pg)+Fypg)
7,423,200N=0.83(0.65)0.8(360,000mm2)[0.85(35MPa)(1-pg)+(14MPa)pg]
=155,376mm2[29.75MPa(1-pg)+(414MPa)pg]
=155,376mm2(29.75MPa-(29.75MPa)pg+(414MPa)pg)
=155,376mm2(29.75MPa+(384.25MPa)pg)
=4,622,436N+(59,703,228N)pg
7,423,200(N)-4,622,436(N)59,703,228(N)=pg=0.04690.010.08(okay)
Determine the required steel area
Any of these selections would be appropriate. The most economical choice based on labor
would be the 1636M bars, which require less time to erect the system.
Select the ties. With 36M bars, the minimum tie diameter is 13M.
Maximum tie spacing =16db=16(36mm)=576mm
Maximum tie spacing =48dt=48(13mm)=624mm
Maximum tie spacing = minimum column dimension =600mm
The first tie spacing value must be used, which can be rounded to 570mm. For lateral brac-
ing, longitudinal bars must comply with minimum distances from tie corners, as shown in the
illustration.
36M bar dia. =36mm
Minimum spacing =38mm
1.5db=1.5(36mm)=54mm>38mm
Check bar spacing:
Cover 2(38mm)=76mm
Five bars (36mm)=180mm
Min. spacing 4(54mm)=216mm
472mm600mm(okay)
The tie requirements indicate that no bar may be more than 150mm from a tie corner, so
we will need to insert a second tie at each location as shown to meet this requirement. A
"corner" is defined as an angle of 135 or less.
Use a dead load factor of 1 . 2 5 and live load

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Civil Engineering Questions!