Question: A 5 0 - MVA, 1 2 . 5 kV generator has a direct - axis sub - transient reactance of 0 . 2 5

A 50-MVA, 12.5 kV generator has a direct-axis sub-transient reactance of 0.25 per unit. The negative- and zero-sequence reactances are, respectively, 0.35 and 0.10 per unit. The neutral of the generator is solidly grounded. When a single line-to-ground fault occurs at the generator terminals with the generator operating unloaded at rated voltage, determine (a) the sub-transient current (in amperes) in the generator, and (b) the line-to-line voltages (in kV) for sub-transient conditions.