Question: CHAPTER 2 0 Special - Purpose Outlets for Ranges, Counter - Mounted Cooking Unit ( 1 3 . ) For ranges of 8 3 4
CHAPTER SpecialPurpose Outlets for Ranges, CounterMounted Cooking Unit
For ranges of or higher rating, the minimum branchcircuit rating is amperes.
A nonmetallicsheathed cable is used to connect a wallmounted oven. The insulated conductors are AWG. What is the size of the equipment grounding conductor in this cable?
Match the following statements with the correct letter. Some letters may be used more than once.
A ampere, wire receptacle
a for the equipment grounding conductor
A ampere, wire receptacle
b for the white neutral conductor
The Lshaped blade on a
c for the "hot" ungrounded conductors ampere plug cap
d NEMA R
The horseshoeshaped slot on a
e NEMA R
ampere receptacle
f NEMA P
A ampere, wire plug cap
Terminals X and Y
Terminal W
Terminal G
When connecting an appliance that is made to foreign standards and is being connected in this country, it is circle one:
a important to verify the terminals to be used for the supply conductors to be certain the connections are proper.
b likely that color coding of conductor insulation colors is universal so no concern for colorcoding is needed.
A receptacle is mounted inside of a kitchen cabinet for the purpose of plugging in a microwave oven. Circle the correct answer.
a The receptacle is permitted to be connected to the same circuit that supplies the other receptacles that serve the countertop areas.
b The receptacle is not permitted to be connected to the same circuit that supplies the other receptacles that serve the countertop areas.