Question: Figure 2 3 0 . 2 6 1 Wire connected to the motor must have the correct ampacity according to the 7 5 column. However,

Figure 230.261
Wire connected to the motor must have the correct ampacity according to the 75 column.
However, inside the conduit between the panel and the wireway ampacity corrections are made, as usual, in the 90 column. The specifications require that separate equipment grounding conductors be installed in each raceway. The engineer who wrote the specs means that a metal raceway can't be used as the only EGC. But remember that only one EGC must be installed in each conduit.
Refer to the drawing shown below to answer questions that refer to this figure.
Refer to Figure 230.261. The smallest circuit conductors that can be installed between the wireway and the safety switch for Motor #2 are q, AWG.
Select one:
a.8
b.10
c.6
e.14
Figure 2 3 0 . 2 6 1 Wire connected to the motor

Step by Step Solution

There are 3 Steps involved in it

1 Expert Approved Answer
Step: 1 Unlock blur-text-image
Question Has Been Solved by an Expert!

Get step-by-step solutions from verified subject matter experts

Step: 2 Unlock
Step: 3 Unlock

Students Have Also Explored These Related Electrical Engineering Questions!