Question: Problem 3 : Given: Floor Structural Framing plan is shown below. The floor is constructed of 4 in . thick reinforced concrete and supported with

Problem 3:
Given: Floor Structural Framing plan is shown below. The floor
is constructed of 4 in. thick reinforced concrete and supported
with W14 x 22 spaced 5 ft . on center and must support a
uniform live load of 100 psf . There will be moveable steel
partitions on the floor and a suspended ceiling below. Include 10
psf of dead load for miscellaneous utilities supported by the
structural steel and a carpeted floor finish.
Find: Maximum design load on the interior beams (plf) using
ASD and LRFD methods according to ASCE 7-22.(20)
Problem 3 : Given: Floor Structural Framing plan