Question: Problem 4 Refer to RC - 0 2 for simplified calculation for shear. Given: Column diameter, D = 6 0 0 m m Longitudinal steel,

Problem 4
Refer to RC-02 for simplified calculation for shear.
Given: Column diameter, D=600mm
Longitudinal steel, Ast=8x28mm bars wfy=415MPa
Lateral ties, 12mm with fyt=275MPa
Concrete (normal weight),fc'=27.5MPa
Shear strength reduction factor =0.75
Factored axial compression force =3,000kN
What is the shear stress area of concrete, in mm2? Ans: 288,000mm2
What is the design shear strength of the concrete along the x-
direction, in kN. Answer=338.50kN
What is the design shear strength of ties, in kN, if the spacing of the
ties is 75mm. Answer=298.57kN