Question: Question # 2 A close - in SLG fault on FDR 2 3 , generates 1 8 kA , with an (

Question \#2
A close-in SLG fault on FDR23, generates 18 kA , with an \(\mathrm{X}/\mathrm{R}\) ratio of 17. If the goal of the design is to avoid CT saturation, evaluate the performance of the existing CT tap shown on the drawing. If you find the CT tap inadequate, select the minimum CT tap that can be used. Demonstrate mathematically or graphically (using the PSRC spreadsheet) that your choice works. Assume the total cable impedance for the CT is 1.1 ohms. You may use the CT excitation curve, for a C800,2000/5 CT used in class for this question.
Question \ # 2 A close - in SLG fault on FDR 2 3